coloradog1
Mining
- Apr 24, 2007
- 35
Hello guys. Need some help. We are currently getting the following readings off our relay. Phase rotation is acb.
Ia=100A < 0 deg
Ib=100A < 180 deg
Ic=100A < -120 deg
The voltage readings from the relay are correct. This is obviously giving us both zero sequence and negative sequence currents. Both phase A and C currents look correct. My question is, can someone explain why phase B is giving the angle of 180 degrees. It should be giving about 120 deg. Our thought was that the CT polarity might be reversed, although we don't know this yet. However, if it was reversed I would assume this would change the angle from 120 deg to -60 degrees (120 minus 180), not 120 to 180. Any help anyone can give would be appreciated.
On a similar note, if anyone has a document or spreadsheet that helps simulate CT wiring problems and the corresponding currents that would result, I would appreciate that also.
Thank you very much.
Ia=100A < 0 deg
Ib=100A < 180 deg
Ic=100A < -120 deg
The voltage readings from the relay are correct. This is obviously giving us both zero sequence and negative sequence currents. Both phase A and C currents look correct. My question is, can someone explain why phase B is giving the angle of 180 degrees. It should be giving about 120 deg. Our thought was that the CT polarity might be reversed, although we don't know this yet. However, if it was reversed I would assume this would change the angle from 120 deg to -60 degrees (120 minus 180), not 120 to 180. Any help anyone can give would be appreciated.
On a similar note, if anyone has a document or spreadsheet that helps simulate CT wiring problems and the corresponding currents that would result, I would appreciate that also.
Thank you very much.