OK -
This middle aged field guy has an "in service test" for proving CT's and associated wiring for a Hi-Z Diff scheme.
I only recommend that this be performed by experienced and qualified field personnel who are good with hand tools.
**********************************************************
NO I am NOT CRAZY, I know what I am doing.
**********************************************************
I am assuming you have back up OC protection and some flexibility in switching. I would recommend setting the back up OC more sensitive. Any other overlapping Zone protection could also be set more sensitive.
The 87B trips from the lock out (86) relay will have to be disabled for the test. As a matter of fact, the audible sound of the 86 will speed things up. I would certainly verify that there are absolutely no 'sneaky circuits' in the 86 tripping scheme. It wouldn't hurt to verify that there are no DC grounds prior to commencing with the test.
#1 - 87Z theory - assuming that all secondary wiring and the CT ratios / polarity are correct, there will be no diff current at the 87 relay terminals, under load. The only way to prove this scheme (the anti test) is to create a false diff current / voltage and let the relay trip the lock out (86) device. Utilize load switching if you have a by-pass / maintenance breaker for double bus arrangements. This
***********************************************************
NO I am NOT CRAZY - I know what I am doing
***********************************************************
The idea of the test is to open circuit the CT at each summation point. Yes, I said open circuit the CT.
Use insulated needle nose pliers and a holding screwdriver. It only takes a second. Hold the lug / wire with one hand (in insulated pliers) and the holding screwdriver with the other - lift the wire just a little bit. You will expect to
see arcing and hear the 86 roll. The wire only has to be lifted just enough for an arc to develop. For those who are interested, there is a time constant for a dangerous voltage to develop. For the 30 cycles that you are lifting and the relay is operating only a few hundred volts will develop. I would guess that David Beech could fill us in on the exact formula.
For those still concerned about personal safety, the MOV's (or metrosils) will generally clamp at ~600V or so, which I believe will satisfy OSHA (or other local safety bodies) if you are wearing Class 0 hot gloves and properly rated insulated tools.
That proves the rest of the CT's in the scheme. Repeat for every CT that is included in the summation of the 87Z scheme. You may need a helper and two way radios if the CT's are paralleled in a marshaling cabinet in the switchyard, which is the proper location for this scheme. Have the helper confirm the trip and reset the 87 and 86 relays after each CT is tested.
In my experience, it takes longer to explain what you are doing to those who do not understand the 87Z scheme than to perform all the tests in the scheme.
************************************************************
Just keep explaining that you are NOT CRAZY and understand what you are doing.
************************************************************
The primary injection scheme proves restraint for through fault conditions, by making an open circuit, sufficient voltage and current is developed to test the MOV's, the relay 87H and 87L element and the trip to the 86 device.
***********************************************************
This was a 'patented trick' I learned from another OFG some years ago.

I am passing this trick on as I enjoy the quality of the discussions on this board with some obviously sharp engineers and field technicians.
The first time I did it, my heart was pounding and I was sweating like a pig.
I commissioned 2 8 breaker ring buses with 587Z and MFAC relays using this method in about 4 hours some years ago.
************************************************************
All the best!