Dear Gentlemen
Can anyone please help me.
I have an electrical system with the next data:
X/R: 15.3; If=14500A; Vsys=10kV
The installation will include a MV Switchgear
I'm thinking of using a Feeder Protection Relay with the next:
-CT rating/Maximum Transient: 80xInom=400A for 1sec
-CT Burden<0.25VA@5A
The resistance of the leads from CTs to the relay is 0.026Ohm aprox. Moreover I have 03 Flex Core CTs C200 800:5A With secondary winding resistance 0.706 Ohms@75°C
I'll apreciate so much if you can tell me if my selection is all rigth or CTs will saturate due to 14500A (SC Current)