Here is an extract:
IEEE standard C57.13.3 serves as the ANSI guide to standardize instrument transformer grounding practices. The grounding of CTs is important to both safety and the correct operation of protective relays. To assure safe and reliable operation, the neutral of the CT secondary should have a single ground location for each circuit. The single ground is irrespective of the number of CTs or the chosen grounding location. Utilizing a single ground eliminates the risk of redundant ground loops and associated problems.
During normal operation more than one ground on a CT circuit is not an obvious problem, other than the difficulties it may cause during testing. However, during a fault condition, multiple grounds allow a different ground potential rise for each CT. The result is a significant current flow through the CT circuit that is not representative of the primary current.