I am not familiar with the term saturation test but it seems from the above posts like an exciting current test to obtain the knee-point of the CT. With this test you can also obtain the exciting curve (mag-curve) of the CT.
You'll need a variable voltage, (easiest obtain from a variac - must be able to obtain the suitable voltage) a voltmeter, an ammeter, a pencil and paper.You'll have to measure the voltage and the current while you do the test.
Apply the voltage to the secondary winding with the primary and other windings being open-circuited. Increase the voltage until you reach a point where a small increase in voltage results in a big increase in current.
Now slowly decrease the voltage to a few measuring points, while you measure the current. (write it down) Something like:
205V - 1.1A
200V - 0.6A
190V - 0.238A
180V - 0.149A
170V - 0.114A
150V - 0.08A
125V - 0.061A
100V - 0.049A
50V - 0.028V
25V - 0.017A
0V - 0A
You have to decrease your voltage slowly to zero volt to demagnetize the CT-core.
BEWARE The knee-point voltage will depend on the size and class of the CT, and it can be very high on some CTs (several hundreds of volts) Be very cautious, you will be working on live equipment during the test.
Now you can just plot the current and voltage values on a graph. This is the mag-curve of the CT. IEC classify the knee point voltage as the point where a 10% increase in voltage results in a 50% increase in current.
[red]Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon[/red]
Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376
