Bigmantony, et al...
Was wondering why you want to measure the remanence of the CT anyway?? Depending on the ratio, type and physical size you may be able to view the B-H curve direct with a scope and simple integrator, provided you also have the means to excite the core. If you are still interested, give me some speific details on the CT in question and I will see if I can help you.
BTW, I do not think that electricpete was saying to open circuit the CT, but just to compare the exciting current at some known or typical curve value to see if remanence is present. In some cases you can determine that and once the CT is driven into saturation and slowly reduced back to zero, the remanence will be removed.
And I agree that you should never open circuit the secondary while the primary circuit is energized, for several reasons. First and foremost, the open circuit voltage developed can be hazardous to personnel. And could damage the CT winding in the process, or at least magnetize the core.