Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

CT Ratio Selection

Status
Not open for further replies.

Cerkit

Electrical
Joined
Jan 18, 2016
Messages
100
Location
GB
Hi,

I am looking at a 22/400kV 600MVA transformer. I am looking at CT sizes for the LV side of the transformer. For full load current the current is 15745A. Is it possible to use a 16000/1 CT or does this ratio of CT not exist?

Thanks
 
@Cerkit,
What is that CT for? AFAIK, at that range, you can find bushing CTs for that. If you wanted a CT for metering, a 16,000/5 is fine. If you want to use it for protection, a 22,000/5 would be better.
 
I have worked with 19000/1 CT's for a 660MW generator for protection purposes. But yes, what are the CT's for? If for protection please state what kind of protection.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top