tem1234
Electrical
- Jun 13, 2007
- 192
Hi,
While testing polarity check on transformer ct and the battery applied to the primary, a dangerous voltage and arcing may be generated while disconnecting the battery from the transformer winding. This happened to a very experienced technician last week.
I just want to be sure that i understand why this happen. Is it that the reactor of the transformer is opposed to current variation.
This isn't happening habitually, but this time a 36 V instead of a lower voltage battery was used because of some reading problem by the ampmeter connected at the secondary.
How do you check polarity safely?
Thanks
While testing polarity check on transformer ct and the battery applied to the primary, a dangerous voltage and arcing may be generated while disconnecting the battery from the transformer winding. This happened to a very experienced technician last week.
I just want to be sure that i understand why this happen. Is it that the reactor of the transformer is opposed to current variation.
This isn't happening habitually, but this time a 36 V instead of a lower voltage battery was used because of some reading problem by the ampmeter connected at the secondary.
How do you check polarity safely?
Thanks