With omicron CT analyser we tested 2 220KV cts,
one having Kx 26 & other having 75
both are having Knee point #voltage 1600 (Name plate),
actual 1800&2400respectively,
one is STR=26.1 other 40KA
during a fault of 34KA what will the difference in behaviour of CTs ,is there any chance of CT saturation?
here we came across with question of Kx and Ktd(Over dimensioning factor)can you explain?the Cts are used in Bus Differential protection,oneof the CT is suspected to have malfunctioned during a flashover fault.