Keith,
PLEASE. Any valve wastes energy, just as any VFD wastes energy (remember at least 4 or 5 percent just due to VFD inefficiency, at lower flowrates MUCH more due to even lower motor and VFD inefficiencies at partial loads). Your statement shows about as much unwarrented favoritism for VFDs as the Cycle Stop Valve guy had for valves. Which option wastes LESS energy is the question that should be answered.
Gare,
As I said above, the CRITICAL question to be answered when designing all systems is which option will waste LESS energy when considering all the flow and head requirements of the system and the manner in which the system will be operated throught its entire lifetime. For a system that has little static head variation, but will be operated only at one flowrate, or within a narrow flowrate and head margin, it will pretty much ALWAYS be more efficient WITHOUT a VFD sapping off energy. In fact, you might not even need a valve. Same goes for a system that has high static head requirements at all flowrates.
For a system that has head requirements that vary with the square of speed and wide ranges of flowrates, you could consider a vfd, provided that there IS a wide range of required flowrates. For a system that has high static head requirements at most flowrates, VFDs are not even an option.
I've spent most of the past year analyzing many cases of VFD vs VALVE or NO VALVE and can say with a very high degree of authority, VFDs are not the panacia many think they are. In fact, as a rule of thumb in many systems, work well only between 50% to 80% of what would be the BEP flowrate and speed of a single speed pump installation, given that the variable head they produce at reduced rpm still allows those partial flowrates in the system. That "work well" criteria includes a necessity to operate in that 50% to 80% range for a significant portion of the systems lifetime. Many times it is a very close call, in which case maintenance concerns for VFD related symptoms of bearing and power quality problems often tip the balance to favor not using a vfd. The whole point being here is that, if you fall outside some very small margins of my rules of thumb, a general question about VFD vs Valve cannot be answered without a very carefull and sometimes a very detailed analysis of your specific system and how it will be operated.
A perfect example of what kind of system it is and how it will be operated is to consider an irrigation system, which often have high static head requirements if the pump is lifting from a well, so VFD may not even be an option. Secondly, and most importantly, in an irrigation system, WHY do you even need variable flow? Why not just water the plants using one flowrate and turn off the pump when they get enough, or switch to a different field? That's how I handle my grass. Do you need to water one lawn at 2 gpm and the other at 5 gpm? You could water lawn 1 at 1 gpm for 2 hours and the other at 1 gpm for 5 hours. Other options might be to build a tank, pump at one flowrate until the tank is full, then turn the pump off and trickle flow from the tank. Why use a VFD to get trickle flow? IMO, irrigation is perfectly suited for single speed operation, no VFD no VAVLE.
IMO, in irrigation systems, cycle stop valves are best used for hammer prevention and adjusting head and flow, but to a lesser estent. Stopping hammers will also stop-short a lot of maintenance problems with broken pipe joints and initiating pinhole leaks. Their biggest advantage in an irrigation system is they can do that without using a VFD, which I believe are basically not necessary in such a system. If you have an industrial process where you have to feed glue, or some other fluid, from the same spout at many flowrates go VFD. If you have a water demand that varies alot, but you can't turn on or off 1 to 4 pumps, get a VFD, but only if your required head also varies accordingly. If head remains relatively the same, use a valve, or don't use a valve if you don't need it. VFD, use them if you need them, if you don't... don't.
**********************
"Pumping accounts for 20% of the world’s energy used by electric motors and 25-50% of the total electrical energy usage in certain industrial facilities."-DOE statistic (Note: Make that
99% for pipeline companies)