juventus7597
Specifier/Regulator
- May 12, 2009
- 1
Hello All,
I am assessing an over voltage situation where a home owner's tv's, stereo equipment etc. failed and overheated when a temporary above ground electrical service cable, connected from the utility's transformer to the service meter, was energized. (Due to a problem with the existing underground service cable which required repairs, the above ground cable was used to temporarily supply power to the dwelling while allowing for repairs to the underground cable).
As the temporary cable was energized, various electric and electronic devices in the dwelling overheated with smoke noted to be emanating from tv's!
Everyone knows of the potential "floating neutral" condition and related voltage imbalances that could occur in 120V circuits. But my question is the following:
If one of the incoming line conductors in the temporary cable was mistakenly connected to the neutral terminal in the service meter, with the incoming neutral conductor connected to one of the line terminals in the meter, could this have applied 240 Volts to various 120V circuits in the dwelling, leading to the overheating/failure? Thanks in advance!
I am assessing an over voltage situation where a home owner's tv's, stereo equipment etc. failed and overheated when a temporary above ground electrical service cable, connected from the utility's transformer to the service meter, was energized. (Due to a problem with the existing underground service cable which required repairs, the above ground cable was used to temporarily supply power to the dwelling while allowing for repairs to the underground cable).
As the temporary cable was energized, various electric and electronic devices in the dwelling overheated with smoke noted to be emanating from tv's!
Everyone knows of the potential "floating neutral" condition and related voltage imbalances that could occur in 120V circuits. But my question is the following:
If one of the incoming line conductors in the temporary cable was mistakenly connected to the neutral terminal in the service meter, with the incoming neutral conductor connected to one of the line terminals in the meter, could this have applied 240 Volts to various 120V circuits in the dwelling, leading to the overheating/failure? Thanks in advance!