Cross-Bracing

Status
Not open for further replies.

dik

Structural
Apr 13, 2001
26,056
I typically use kl/r for rod x-bracing = "0.45 times the diagonal length / r" with a U-bolt at the intersection and a max kl/r of 300 as per Canadian Steel Code. There is provision to waive this if other means are provided to eliminate flexibility, sag, vibration or slack...

What do members of this forum do? Any published info on this?

Dik
 
Replies continue below

Recommended for you

I think that the KL/r is more or less a recomendation (at least in AISC). If you properly design the rod as a tension member and check your appropriate limit states, you should be fine.

Is the U-bolt connecting the rod to a plate? You could also use a length of rod equal to the diagonal distance of the bay and turnbuckles in the middle as well. Thats what I typically see in pre-engineered metal bldgs. I've also done this in mezzanine structures as well
 
Thanks... the U-bolt is at the intersection to keep the two bars from rattling.

Dik
 
I designed elevated water tanks for years. KL/r was not an issue for us as the rods had turnbucles to taking out the slack. Rods were sized fof tension loads only, so the area requirement determined the rod diameter. Rods of 50 to 70 feet in length were very typical.

Joe Tank
 