davidyu2404

Mechanical
Jul 23, 2015
11
I am a little bit confused on this: After pressure balance by design, how could there be a critical path (since all paths have the same pressure loss now)? I am designing a local exhaust system and each path starts from the terminal to the exhaust fan.
 
Replies continue below

Recommended for you

Critical path is the one with balancing damper all open if they did it right.

All paths will have equal pressuredrop - no matter what. Problem is, this is not the flow you want. So you use dampers to reduce the flow while keeping pressure the same in all runs.
 
Critical path is usually but not always the longest run.
 