The Nationoal Electrical Code 2011 Chap 9 Table 8 Conductor Properties: 16 AWG, not stranding, copper and coated: 16.7 ohm/Km. The cable run is 60 m then we have 1.002 ohm but our measure is 4.1 ohms, the instrument calibration is ok, we are looking a "criteria acceptance" for "continuity check" to reject this circuits.
Thanks