For buckling of web members in the plane of the joist, the computed effective length factors
ranged from K=0.50 to K=0.55. This indicates a significant amount of rotational restraint exists
at the ends of the compression web members, which can be shown to be the byproduct of
assuming fully restrained (rigid) connections and having top and bottom chords with in-plane
flexural stiffnesses that are much larger than that of the web members. The overall performance
of K-Series joists was similar to that of LH-Series joists, which indicates that the SJI may be
justified in allowing K-factors for both types of joists to be less than unity (see Table 1). Unless
the connections are specifically designed for the demands associated with using K-factors close
to the rigid-rigid case of K=0.5, the SJI’s value of K=0.75 for LH-Series joists seems reasonable.
A much wider range of out-of-plane effective length factors (K=0.52 to K=0.87) is observed,
with most values between K=0.5 and K=0.75. Given that web buckling out of the plane of the
joist is primarily resisted by the relatively smaller torsional stiffness of the top and bottom
chords, K-factors larger than the in-plane values would be expected. Because the ends of the
web members are almost always located (pinched) between the angles comprising the top and
bottom chords, the SJI’s assumption of K=1.0 (see Table 1) for out-of-plane buckling appears to
be conservative, and similar studies of additional joists may indicate that a value of K=0.85 or
K=0.90 could be used in routine design.