You do not say whether this is a new or existing house.
1. CONDITION: Wet walls / No leakage on floor (NO DISPLACEMENT)
Characteristics:
Water spots on walls, wet walls, walls periodically dry up usually leaving scale stains, efflorescence, or mildew. Damp spots either high or low on wall. No major cracks or bowing. No significant block deterioration or displacement. No leaning of walls. No movement in footing.
Testing:
Check palmer valve or sump pump for correct operation. Check with local jurisdiction if palmer valve is permitted (per local requirements).
Break open floor, test interior drain tile for correct flow to palmer valve, or sump pump.
Use water spud pipe, inserted along outside wall to exterior drain tile, to introduce water to check exterior drain tile operation.
Check for proper grade away from exterior walls and adequate gutters & downspouts.
Standard Repairs:
Extend downspouts, improve grade by increasing pitch away from buildings to the greatest extent possible.
Install, replace, or repair sump pump. Sump pump must meet State and local Plumbing and Electrical Code.
Replace some or all of interior drain tile as necessary, drain first block into interior drain tile using an approved one-piece wall drainage board that provides water passage and lateral support to first course of block. Wall drainage board to be 1" minimum higher than floor. Use a wall drainage board that can be caulked for retarding radon migration. Install to manufactures specifications. See Appendix B & C.
In some cases it may be necessary to excavate to footing, seal wall, clean out bleeders, replace exterior drain tile, backfill to within 12-18" of grade with clear stone backfill. See Appendix A.
Maintenance After Repair:
Keep downspouts extended.
Maintain positive pitch of grade away from house.