I have been using the PCA Rectangular Concrete Tanks book to design some WWTP tanks, as well as, other tanks. I have developed some questions based on the procedure. I am looking for others experience to get a feel for the final design.
My concern is with the Crack Control req'd steel. I am required to maintain 3 5/8" cover on the steel when I compute the stress in the steel. This is due to the DeNeef Swellseal bead to protect the steel at the cold joint and make the tank water tight. The bead requires 3" of cover and the bead is to be 5/8" in order to maintain a waterproof joint. Because of this, my max spacing for the rebar to control cracking ends up being less than 4" (unreasonable). The only way I can see to fix this problem is to increase the size of my wall or reduce the cover on the steel. My tank is a small 12'L x 8'W x 12'H tank. I have been trying to maintain a 12" wall. It just seems excessive to increase the wall thickness to 1.5' just to increase the steel spacing.
The other problem I have is the buoyant force. The WWTP is located on the side of a hill, so I don't see how the soil could become saturated long enough to lift the tank, but the calculation shows that my FS is less than 1 and I have to increase the walls and slab to be huge to get the F.S. to even be 1. I don't see any other way to make the tank heavy enough to resist the buoyant force.
So, I guess my question, on this small of tank, do you go to the extent of installing helical piers or is there other justification for resisting the buoyant force? Also, is my crack control spacing out of control? I just need a feel for good practice to know whether I am not trying to make the tank too small, and should be looking at thicker walls, slabs, etc. Mass concrete or economy?
Thanks for your comment/sorry for the long explanation!
My concern is with the Crack Control req'd steel. I am required to maintain 3 5/8" cover on the steel when I compute the stress in the steel. This is due to the DeNeef Swellseal bead to protect the steel at the cold joint and make the tank water tight. The bead requires 3" of cover and the bead is to be 5/8" in order to maintain a waterproof joint. Because of this, my max spacing for the rebar to control cracking ends up being less than 4" (unreasonable). The only way I can see to fix this problem is to increase the size of my wall or reduce the cover on the steel. My tank is a small 12'L x 8'W x 12'H tank. I have been trying to maintain a 12" wall. It just seems excessive to increase the wall thickness to 1.5' just to increase the steel spacing.
The other problem I have is the buoyant force. The WWTP is located on the side of a hill, so I don't see how the soil could become saturated long enough to lift the tank, but the calculation shows that my FS is less than 1 and I have to increase the walls and slab to be huge to get the F.S. to even be 1. I don't see any other way to make the tank heavy enough to resist the buoyant force.
So, I guess my question, on this small of tank, do you go to the extent of installing helical piers or is there other justification for resisting the buoyant force? Also, is my crack control spacing out of control? I just need a feel for good practice to know whether I am not trying to make the tank too small, and should be looking at thicker walls, slabs, etc. Mass concrete or economy?