I am trying to spec a disconnect/motor controller for the following motors, all are in class 1 div 1 group D, all are 480 3ph motors
(6) 1hp motor with start/stop only
(3) 10 hp motor with VSD
Since we are in a hazardous location, I am trying to consolidate equipment to save $$
looking at the small 1hp motors:
According to 430.112C, a single disconnect can service groups of motors 'within sight of the disconnecting means' provided 430.110C is satisfied.
It appears that 430.110C specifies the disconnect must consider both full load current and max locked rotor current. Thus for the 6 1hp motors, we are looking at a combined full-load current of 2.1*6=12.6 A, and a locked-rotor current of 15*6=90A.
According to table 430.251(B), this locked rotor current corresponds to a 15HP switch, which also satisfies the full-load current as per table 430.250.
thus a 60A, 15HP heavy duty safety switch such as square-D H362N is acceptable, correct?
ok, now for the tricky oddball code-interpretation question. The hazardous location room is entered by two double doors. The doors constitute an occupancy separation, and thus should have manual or thermal closures. Ideally I would like to place the VSD's for the large motors outside of the hazardous location room on a facing wall. In other words, if the doors were open, the disconnects and motor controls would be 'in sight' as per code. Is this technically incorrect, to assume the doors would be open under normal operation? Otherwise, to gett out of the classified area, I end up having a lot of dead space in the room to get the 8' separation from hazardous area.
I have contemplated providing a large purged and pressurized enclosure to contain the vsds and disconnects as per 500.7D, but fear this may get prohibitively expensive as well.
One final question, would a local start/stop switch or panic button that could break current to the coil on a remote magnetic motor starter be considered acceptable as a local disconnect? Not sure if this would fall under 430.109(A)(1) as a 'HP rated motor circuit switch'. I think thatey mean the larger safety switches as I stated above, but the haz. loc pushbutton control boxes are quite common and affordable.
Thanks in advance, as always!