QCE,
The purpopse of performing the El-Cid after the rewinding is to identify any damage to the core that might be caused as a result of the winding installation, packing, and wedging.
The El-Cid test is one of other tests to be performed in the Field to assure the high quality of work before energizing the machine. Failure of any test could be grounds for the rejection. The other tests are: Winding Hi-pot test per ANSI C50.10, IEEE 95 & 115; Armature (stator) resistance per IEEE Std 115; Insulation Resistance and Polirization Index; and Blackout test after all other field tests have been successfully passed. Also, will add testing the RTDs for continuety and insulation resistance and to insure proper temperature indication. The idea behind all the tests is to cover all the possibilites of failure before the start-up, and loading the machine.
Hope this will help. Regrads.