coping bottom flang of wide flange beam 1

Status
Not open for further replies.

Jumbo55R

Structural
Dec 2, 2009
2
I need to reduce the depth of a W24x131 beam by 5" for approximately 3'-8" at one end. The beam doesn't allow for sufficient headroom at a ramp below. The total beam span is 35'-2". I am considering coping the bottom of the beam by 5". The 5" cope won't interfere with the end connection.
Can someone help me with what checks must be made?
 
Replies continue below

Recommended for you

I would simply make the cope, weld back a flange plate of the same width and thickness as the beam flange, slotted around the web for about a foot, and call it good. Do the numbers, but that will work, and it will look right.
 
Jumbo:
There shouldn’t be any problem in doing that, just check the beam stresses at each of the transition points. And, the end connection design will change a little as a function of the shallower beam at the end. Pay some attention to detailing and welding details as these relate to any fatigue issues. The bending stresses are pretty low at that location in the beam span, although the shear stresses are somewhat higher. Talk with a couple fabricators about how they would prefer to do this in their shop. You could also taper the flange on both sides to a somewhat smaller width if you wished. There are basically two ways to do this:

Out at about 5' you saw cut the bot. flg. You want a gradual transition slope. Then you cut the web to the desired coped shape with the deeper transition starting at the flg. cut, and the upper transition, with a nice radius, at about 3'-8" and up about 6". You bend a new bot. flg. and weld it to the existing bot. flg. and then to the web. This bot. flg. weld is the critical detail, it should probably be full pen. and the two flgs. blended together in thickness and width. You might want to provide a web cut-out (see AISC typical details for beam flg. moment connections at heavy columns) so you can back gouge the top of the flg. weld and reweld it, under the web. Also, at the upper transition, note that the flange forces tend to pull the flange away from the web, so for 6" or so on either side of this transition increase the size of the web to flg. fillet welds a bit. One way to do this is to provide web bevels in this transition region, then fill the bevels and do the normal web/flg. fillet welds over the bevels.

Alternatively, cut the coped shape out of the web and just above the flg., and clean up the existing flg. in the area of the web/flg. radii. Then over bend (slightly) the upper transition into the flg., and finally bend the flg. up at the lower transition to match the web shape. This bending is usually done by heating the flg. at each bend area, and using typical fab shop bending equipment. Finally, make the web to flg. fillet welds, starting at the lower transition and working to the end of the beam. Note that these web/flg. fillet welds will seldom have to be as large as the radii in the rolled shape.
 
A W24x131 on 35' may have a fair shear reaction to generate that section... a matter of checking the shear stress, too...

Dik
 
Thanks for these thoughts. I intended to check bending and shear stresses, but I wasn't sure if I was missing an AISC required check or restriction. Your responses are greatly appreciated.
 