aikmeam
Chemical
- Jun 3, 2003
- 20
I've got a concern with a current design work I'm doing now which I hope to hear some opinions.
There are many water cooled heat exchangers in my work, in which the low pressure side (cooling water) pipings are not designed according to API 10/13 rule. And since the high pressure side can be as high as 1500# rating, we've installed bursting disk to prevent overpressure of the cooling water side in case of tube rupture in favour of its quick reaction time as compared to PSV. The setting of the bursting disk has been such where nuisance rupture can be avoided.
The tail piping of the rupture disk has been routed to flare as there might be a possibility of flammable gas from the high pressure side being relieved. My concerns are:
1. When the high pressure side finally loses its pressure after some time, cooling water will be continuosly drained into the flare, flooding the flare system. A relief scenario based on total plant loss of cooling water will then occur and since the header has already been flooded, there is a potential inability for the rest of the PSVs to vent to flare.
2. Is it really necessary to vent the gases + cooling water to flare? Thinking deeply, tube rupture is a remote case. A leak or pinhole is more likely, and that will not open the disk and eventually the flammable gases will be sent to the open atmosphere through the cooling tower anyway.
In the effort trying to be safe by venting to flare, it seems that like we're creating more hazard. I am thinking if venting it to safe location is a more pratical solution but then again, proving a safe location is indeed safe is not easy. Dispersion, radiation, and god knows what other thorough calculations needs to be done to prove that.
Appreciate anyone with prior experience on this same scenario to share. Thanks.
There are many water cooled heat exchangers in my work, in which the low pressure side (cooling water) pipings are not designed according to API 10/13 rule. And since the high pressure side can be as high as 1500# rating, we've installed bursting disk to prevent overpressure of the cooling water side in case of tube rupture in favour of its quick reaction time as compared to PSV. The setting of the bursting disk has been such where nuisance rupture can be avoided.
The tail piping of the rupture disk has been routed to flare as there might be a possibility of flammable gas from the high pressure side being relieved. My concerns are:
1. When the high pressure side finally loses its pressure after some time, cooling water will be continuosly drained into the flare, flooding the flare system. A relief scenario based on total plant loss of cooling water will then occur and since the header has already been flooded, there is a potential inability for the rest of the PSVs to vent to flare.
2. Is it really necessary to vent the gases + cooling water to flare? Thinking deeply, tube rupture is a remote case. A leak or pinhole is more likely, and that will not open the disk and eventually the flammable gases will be sent to the open atmosphere through the cooling tower anyway.
In the effort trying to be safe by venting to flare, it seems that like we're creating more hazard. I am thinking if venting it to safe location is a more pratical solution but then again, proving a safe location is indeed safe is not easy. Dispersion, radiation, and god knows what other thorough calculations needs to be done to prove that.
Appreciate anyone with prior experience on this same scenario to share. Thanks.