Dec 10, 2019 #1 WilliamTz Mechanical Joined Dec 13, 2017 Messages 38 Location US I have some large cooling tower currently being installed....4000kW of cooling Would you typically have expansion bellows on the pipework in/out of the towers..? 200dia, 400 dai typically
I have some large cooling tower currently being installed....4000kW of cooling Would you typically have expansion bellows on the pipework in/out of the towers..? 200dia, 400 dai typically
Dec 11, 2019 1 #2 quark Mechanical Joined Jan 23, 2002 Messages 3,409 Location IN No. If they are FRP Towers, you need to support the piping in such a way that the load will not damage the tower. Upvote 0 Downvote
No. If they are FRP Towers, you need to support the piping in such a way that the load will not damage the tower.
Dec 13, 2019 #3 SAK9 Mechanical Joined Apr 12, 2002 Messages 607 Location AU If the towers sit on spring vibration isolators,you need to do a flexibility analysis of pipe work and make sure it can take the tower movement.The easy way out is using a flexible connection ! Upvote 0 Downvote