Thanks Bimr for your help and interest. I´ll try to explain the global picture in order to give you a better understanding.
1- We take the water from a secondary wastewater treatment step that already exits without nitrification denitrification process.
2 - We plan to built a tertiary treatment to reduce colloidal, suspended solids, BOD, pathogenic microorganisms based on coagulation, floculation, filtration, desinfection and phosphorus elimination by chemical precipitation process. So no action on NH4. This will be the make up water for our cooling water.
3 - We plan to control biological growth and biofouling in the cooling tower by means of Chlorine dioxide. So no nitrosomonas & nitrobacter will be alow.
4 - We are trying to avoid a biological treatment of NH4 as is very space consuming and because we need a very reliable system, bacterias are quite capricious
5 - 2750 ?S/cm is the conductivity of this water, this is the reason of concentration factor selected