jfpe
Electrical
- Jul 18, 2007
- 104
I'm working on a job where the utility wants the ability to remotely turn off two solar inverters remotely. The utility will run fiber to the inverters. I don't know what communications protocol they will use.
The question I have is how to convert from a signal on fiber to the trip signal the inverter will accept. The inverters are from different manufactures and accept different inputs
Inverter #1 - Trips based on the opening of a normally closed dry contact
Inverter #2 - Trips based on a Modbus command given over Modbus RS-485.
I don't have a communication background, so I would appreciate any insight on what kind of device is needed to get from fiber optic cable to the trip signal the inverters can read. I expect we'll be pulling in a consultant on this, but I'd at least like to get a little background myself first.
Thanks,
jfpe
The question I have is how to convert from a signal on fiber to the trip signal the inverter will accept. The inverters are from different manufactures and accept different inputs
Inverter #1 - Trips based on the opening of a normally closed dry contact
Inverter #2 - Trips based on a Modbus command given over Modbus RS-485.
I don't have a communication background, so I would appreciate any insight on what kind of device is needed to get from fiber optic cable to the trip signal the inverters can read. I expect we'll be pulling in a consultant on this, but I'd at least like to get a little background myself first.
Thanks,
jfpe