Perhaps I do not understand the meaning of automatic shutdown valve...
But if you are expecting this valve to automatically shut down on an emergency situation, e.g. a plant trip that requires a fast isolation of the system you have to make sure that the supplied actuator is springloaded to the closed position when the actuator is de-energized (no power, pressure, any energy applied).
This also opens another can of worms... can your system withstand a sudden valve shut-off? i.e. what about transients, pressure surges, water-hammer effect etc...
If emergency shutdown is not an issue... then the actuator can be slow opening and closing...but I would spec it out with limit switches to detect open closed positions as well as torque limit, but seems like this has been thoroughly covered before.
HTH
Saludos.
a.