Small 9 MW wind farm is connecting to a 44kV distribution line. The power utility requires that at the point of interconnection, the wind facility maintains a fixed power factor of 0.97 at all times (inductive, the wind facility imports reactive power from the utility grid).
There are 4 turbines, with full a AC/DC/AC conversion, capable of operating in the power factor regulation range of +/0.90, measured at the LV side (inverter output), and where the PF and/or voltage control takes place in the inverter itself.
The collector system is 34.5kV, so each turbine is equipped with a step up transformer and there is also common 44/34.5kV transformer at the interconnecting substation.
Some wind turbine suppliers can also provide a common controller, a sort of common AVR, which is located at the interconnecting substation, connected to station PTs and CTs, and which can be operate the wind facility in either fixed voltage mode or fixed power factor mode. The controller communicates to individual wind turbines via a communication link (usually FO) and sends signals to local inverter controllers.
However, it this particular case the wind turbine is unable to supply such “common” controller at the interconnecting substation, so a system with the same functionality would have to be designed using standard third party equipment, i.e., power factor/voltage monitoring devices, capable of sending an appropriate feedback signal to each turbine controller to adjust its own power factor to whatever is needed in order to maintain the station PF at the preset level.
Has anyone worked on something similar and can provide some hints? North American market, 60Hz. Thank you.
There are 4 turbines, with full a AC/DC/AC conversion, capable of operating in the power factor regulation range of +/0.90, measured at the LV side (inverter output), and where the PF and/or voltage control takes place in the inverter itself.
The collector system is 34.5kV, so each turbine is equipped with a step up transformer and there is also common 44/34.5kV transformer at the interconnecting substation.
Some wind turbine suppliers can also provide a common controller, a sort of common AVR, which is located at the interconnecting substation, connected to station PTs and CTs, and which can be operate the wind facility in either fixed voltage mode or fixed power factor mode. The controller communicates to individual wind turbines via a communication link (usually FO) and sends signals to local inverter controllers.
However, it this particular case the wind turbine is unable to supply such “common” controller at the interconnecting substation, so a system with the same functionality would have to be designed using standard third party equipment, i.e., power factor/voltage monitoring devices, capable of sending an appropriate feedback signal to each turbine controller to adjust its own power factor to whatever is needed in order to maintain the station PF at the preset level.
Has anyone worked on something similar and can provide some hints? North American market, 60Hz. Thank you.