Depends on who you are explaining it to. When teaching electricians basic protective relaying I basically said:
The secondary of the CT knows one thing, "I need to produce X Amps (Usually 5A)", based on the resistance of the secondary circuit it will produce the necessary voltage to maintain that current flow. Under normal conditions the resistance is only a few ohms, so only a few volts is necessary, if you lift the leads (Open the circuit) the resistance incleases as you pull the lead away, the voltage increases, and you will draw an arc. Then I show the interlocks and shorting block/contacts for a 50/51 relay (Hands on, pass around the class).
Not 100% acurate but gets the point and basic theory across, I would use a different one for Engineers and another one for intro students.