control rooms
bragamor
19
I work in a chemical plant and we want to relocate our control rooms, they are too close from our production facilities.
Does anybody know a company in the houston area that can do this work for us?
Thanks for your help on this one
The major contractors and some minor contractors do this sort of work. Just so that you know, I am with Jacobs and have also been with most other majors. Consider the majors if you need a new building and may relocate existing DCS or supporting materials; or if you buy a new DCS.
Some DCS manufacturers could contract this work if you plan to replace the DCS etc. Buying a DCS shelter could also be OK. The total scope for a control room might not be a sound path.
A few other vendors that we use can do the relocation work. A few vendors supply buildings and can do the relocation work too. I use ENGlobal and Contech for analyzer shelter work but they may be OK for control room work too. Other suppliers are well knows for rack room equipment, DCS/SIS integration etc.
For you to select the type business really need to clarify your total scope. Do you need a new DCS? How about a new UPS? Is this only an operator control room or does it include both operations and the control system hardware? Do you consider remotely located DCS I/O hardware that communicates with the controller? Much more could be discussed. Some really cool operator lighting schemes exist that you might never imagine. Is this large or small? Will there be a plant shutdown? If so, how long; six weeks, more, less, etc.? Did I fail to mention other key issues such as HVAC, air system environmental protection, etc.? Help clarify the job scope and some can help with a bidder list. if really needed we (and not just me) could discuss or email some details that you don't want to be shown here.
thanks for your answer JLSeagull
We need a new building where to put our new control room. We already have a DCS and all the wiring, communication systems and electrical work is going to be done in house.
The control room has to be big enough to fit 10-15 operators that monitor 20 reactors. The work has to be done while the plant is running. This is a chemical plant so we need the control room to be fire proof, explosion proof...and yes we need a new HVAC, etc.
I hope this is enouch data to clarify the scope
If you don't want to move far from the process, consider a "hardened control room". I've used Hunter Buildings for these in the past.
Good luck,
Latexman
Are you already in the Houston area? If not, check on the climate and double the HVAC. How hazardous are your chemicals or can you say what the hazards are? Asked differently, what are the risks?
rmw
Blast resistant is another likely term for a control room in a petrochemical plant. Without contacting the civil structure and architectural engineers my guess is a concrete style building with no windows. A purged metal building with about number 10 metal thickness does not seem to be a likely recommendation for 10 operators with technicians and contractors getting permits, checking the restrooms etc. Doors for blast resistant concrete buildings may be large and heavy and perhaps include operating systems to open and close. My concept is that these plant control rooms in the area are even much stronger than the offshore blast resistant control rooms on topwork structures.