Hello friends, have you ever had ghost-like symptoms in your controls panels? What do I mean by that? Here are some examples:
- Indicator lights (LED, 220VAC) flickering when contactors or even regular relays are activated/deactivated.
- Latching relays (for motor control) coming undone in the middle of an otherwise steady pumping run. Just turn off by themselves while steadily pumping.
- Relays driven by external sensors (ie. there is a DC loop going out to a sensor relay, which in turn activates a coil in a panel-local relay, which then participates in the control circuit as an NO/NC contact) activate suddenly in the middle of a pumping run.
Some details about my panel:
-pumps are driven by inverters under PID control (if that matters)
-most of control circuits are 220 VAC, but a few a 24 VDC
-there are a lot of relays and buttons and there are lots of wires to/from in the cable ducts
-I tried my best to separate control and power, but in some places they do intersect (for example near the contactors)
-DC and AC controls share ducts as there is simply no space to separate them
-Analog signals and wires going out to sensors use shielding and are grounded at the panel-side only
-There is only one ground at the panel and it is shared between instruments and motors (I have not yet measured the resistance to ground at the panel. Would it be worth checking?)
-DC relays use diodes on the coils, AC relays and contactors do not
-I have a surge suppressor on the phase that powers the control circuits
Have any of you ever dealt with such symptoms? What could be causing them? How can one go about isolating and diagnosing this behavior?
- Indicator lights (LED, 220VAC) flickering when contactors or even regular relays are activated/deactivated.
- Latching relays (for motor control) coming undone in the middle of an otherwise steady pumping run. Just turn off by themselves while steadily pumping.
- Relays driven by external sensors (ie. there is a DC loop going out to a sensor relay, which in turn activates a coil in a panel-local relay, which then participates in the control circuit as an NO/NC contact) activate suddenly in the middle of a pumping run.
Some details about my panel:
-pumps are driven by inverters under PID control (if that matters)
-most of control circuits are 220 VAC, but a few a 24 VDC
-there are a lot of relays and buttons and there are lots of wires to/from in the cable ducts
-I tried my best to separate control and power, but in some places they do intersect (for example near the contactors)
-DC and AC controls share ducts as there is simply no space to separate them
-Analog signals and wires going out to sensors use shielding and are grounded at the panel-side only
-There is only one ground at the panel and it is shared between instruments and motors (I have not yet measured the resistance to ground at the panel. Would it be worth checking?)
-DC relays use diodes on the coils, AC relays and contactors do not
-I have a surge suppressor on the phase that powers the control circuits
Have any of you ever dealt with such symptoms? What could be causing them? How can one go about isolating and diagnosing this behavior?