panou

Electrical
Apr 21, 2005
33
Hello all.
I want to ask if i can mix single-ended and differential analog input signals in one Control Logix analog input card.
When i tried to do this in an SLC analog input card i had very much noise that dissapeared when disconnecting the differential inputs.
Thanks in advance fro your time.
 
Replies continue below

Recommended for you

panou,

If you are using a 1756-IF8 or 1756-IF16 analog module, you can not mix single-ended and differential modes. All channels on the module must be wired and configured the same way.

Reference Rockwell Automation publication 1756-UM009B-EN-P for everything you need to know about ControlLogix analog modules. Find it at the link below.


(Expand the "I/O" group and select the 1756 ControlLogix I/O link).
 