Have an 8" thick slab on grade with welded wire mesh(WWM). This is a slab for a service area of heavy equipment and vehicles. The slab will have in-floor heating pipes that need to be 2" below the surface and installed above/and tied to the WWM. The minimum depth for saw-cuts is 1/4 of 8" which is 2". This means there is a good chance that the cuts will damage the pipes. Any suggestions or different methods that in your experience worked for doing the control joints safely?
Thanks for the input.
 
Replies continue below

Recommended for you

I would consider increasing the reinforcing in the slab to avoid the need for control joints. We often put the radiant pipes in a non-structural topping slab above the SOG, but if your slab is subjected to heavy loading that may not be appropriate.
 