I’m in the process of building a studio glass furnace and have concerns about the set-up for the control system.
I have 240V single phase
400amps into the building off a 350 aluminum underground line.
Furnace will be on a on a separate 200 amp circuit. Breaker in the box and then fused disconnect 4 feet from the control panel.
Rest of building will draw about a 100amps on their own panel.
2 series of 4each silicon carbide heating elements.
RR 55 x 29 x 1.5 60V each.
Total amps 169 +0/-20 olms: .71 +20/-0
Recommendations by Watlow are:
Controller: EZ-Zone Digi9tal I-O model #PM-9R1 FA-ALAJ-AAA
Multiple Ramp and Guaranteed soak availability.
Temperature and Current limiting
Will have 2 S-type 24gauge, Thermocouples in the furnace
One for regular use and one for over-temp control.
temperatures will be regularly 2130F and (when filling the freestanding pot with glass materials) will be 2350F for up to 20 hours.
The furnace runs 24/7 only shutting down for repairs and a 6 week period in the winter.
SCR : Power series PC-11-F30B-0000
Has a built in fan and fuse.
Some of the questions I can’t seem to get a consistent answer on are:
Element company says no transformer needed.
One Panel builder and Watlow says YES to Tap-transformer if I run the SCR on phase angle. (and should do that to extend the life of the elements.
Other opinions from various engineers:
Can run the furnace on zero –cross (even ssr’s).
Can Run the furnace on SCR zero cross.
Can run the furnace on SCR phase angle WITHOUT a transformer and adjust the ??? as the elements age AND they won’t age prematurely.
Need a safety contactor controlled by the controller between the 240V line coming in and the SCR.
There are more questions, just can’t think of them right now.
ANY THOUGHTS?!?!
I have 240V single phase
400amps into the building off a 350 aluminum underground line.
Furnace will be on a on a separate 200 amp circuit. Breaker in the box and then fused disconnect 4 feet from the control panel.
Rest of building will draw about a 100amps on their own panel.
2 series of 4each silicon carbide heating elements.
RR 55 x 29 x 1.5 60V each.
Total amps 169 +0/-20 olms: .71 +20/-0
Recommendations by Watlow are:
Controller: EZ-Zone Digi9tal I-O model #PM-9R1 FA-ALAJ-AAA
Multiple Ramp and Guaranteed soak availability.
Temperature and Current limiting
Will have 2 S-type 24gauge, Thermocouples in the furnace
One for regular use and one for over-temp control.
temperatures will be regularly 2130F and (when filling the freestanding pot with glass materials) will be 2350F for up to 20 hours.
The furnace runs 24/7 only shutting down for repairs and a 6 week period in the winter.
SCR : Power series PC-11-F30B-0000
Has a built in fan and fuse.
Some of the questions I can’t seem to get a consistent answer on are:
Element company says no transformer needed.
One Panel builder and Watlow says YES to Tap-transformer if I run the SCR on phase angle. (and should do that to extend the life of the elements.
Other opinions from various engineers:
Can run the furnace on zero –cross (even ssr’s).
Can Run the furnace on SCR zero cross.
Can run the furnace on SCR phase angle WITHOUT a transformer and adjust the ??? as the elements age AND they won’t age prematurely.
Need a safety contactor controlled by the controller between the 240V line coming in and the SCR.
There are more questions, just can’t think of them right now.
ANY THOUGHTS?!?!