Continuous Foundation Design

Status
Not open for further replies.

strguy11

Structural
Nov 29, 2005
233
I have a continuous footing under a precast concrete wall. The wall length is 50', and the individual panel lengths are 10'. If the panels are connected together to handle the laterforces, I know I can design the footing as if the wall were 50' long. However, If the panels are not connected together for this shear, can I still design the foundation for a 50' long wall. I would think I could since the forces at the panel ends would be equal and opposite.
 
Replies continue below

Recommended for you

Yes, the result is the same as far as the footing is cocerned a push and a pull at the ends. Check the shear at the panel joints though.
 