Hi,JRLAKE: From your brief report, I'm thinking the starter is a NEMA size 2 or 3 magnetic with a good bit of duty on it. A good check out of the entire control circuit is in order with particular attenion to short cycling issues. Check what voltage you are getting to the coil, its actual connections and physical appearance , condition, You don't want to have more than 3 to 5 % iblevoltage drop thru the motor running overloads . Actually you want near none! Check what the DC resistance is too. Check what the resistance above ground is. Suggest you disconnect the neutral side of the control transformer from ground ( if this is what you have) when you make resistance checks to ground. If possible; you should disconnect the motor legs and using a jumper pull in the starter. See how it operates in these different modes; get a idea of noise , rattle , hum. Open the main (disconnect section) ; don't want any motor power to the starter. Then check , by hand, the mechanical operation- up and down of the main moveable contact set. blow out any fine dust , dirt, rust. Drop the armature out of the coil center. Clean out any dirt, observe any corrosion. You can use a light amount of penetrating oil (say? WD-40) to remove any deep down corrosion to the armature and its guides. As you go thru check and note for better , easier performance. Inspect and lube-clean moveable contact set with (say?-CRC 2-26). When you pull in with ( an external ,other source of coil voltage) the jumper check the DC resistance across each switch closed! Tighten/check all mountings and connections. All brand name (A/B, etc.) starters can easily be totaly or partialy rebuilt. These checks and retrofits are big- buck savings over replacement