gobigorgohome
Has anyone experienced tripping of a magnetic overload protector in a 2 speed motor starter when switching from low to high speed. The units in question have a 3 pole contactor for low speed and a 5 pole contactor for high speed.
This is a new installation with new contactors and motors.
Before everyone gets hung up on contactors closing simultaneously, wiring connections done incorrectly, allow me to ensure that this miserable thing is wired correctly.
Wiring of this unit is consistent with Allen Bradley bulletin 520, variable torque consequent pole. In the literature is states "Motor can be started in High or Low speed. The change from low to high or from high to low can be made WITHOUT pressing the STOP button.
The most interesting phenomenon is that the FLA high speed is 186A, the FLA low speed is 86 amps. The locked rotor current for high speed is 1250A
The MCP that trips is a 250A unit set to the highest instantaneous trip setting of 2500A. We have measured current pulsed through the MCP between 3000 and 4000A!
There are more than one motor and more than one starter exhibing this issue.
Things to note are that:
We have a very low impedance power supply.
Tripping is worse on closer motors (ie shorter field cables)
Are there any motor winders out there that could comment on this being a "normal" phenomenon or could the motors be wound funny?
They run fine at either speed. The pulse occurs with a quick change between contactors or a 2 second both open change between contactors.
There are a number of pretty bright people working on this, just looking for some type of unusual story where someone may have encountered this before.
Motors are 4 / 8 pole, 200 / 50 HP, 575V
Application is cooling tower fan.