Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Connectors in Class 1 Zone 2 Hazardous Location

Status
Not open for further replies.

dinocu

Electrical
Mar 17, 2004
17
Section 18-152(8) of the CEC says:

"Cable glands shall be compatible with the degree of protection and explosion protection provided by the enclosure that the cable enters, where the area classification and environmental conditions require these degrees of protection"

My question is, if I have a cabinet marked as EEx nAde IIC T4, can I use a Teck connector marked as ExeII. Im thinking not.

Also if I have a Class 1 Zone 2 cabinet that is pressurized (Type Z), do the Teck connectors entering the cabinet have to have a sealing compound.

Thanks for your help.
 
Replies continue below

Recommended for you

dinocu,
Your cabinet is EEx nAde. That means it is of non sparking protection, with main protection "d" with increased safety "e" terminals (again non-sparking).Therefore, in my opinion you can use Exe teck cable connectors.With the Type Z, you should have sealing compounds.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor