Does anyone have any tips/comments/advice for connection of steel beams to existing concrete columns with high loads?
Ex. - W36 beam with endplate to 26"x26" reinforced concrete column.
At first, I decided that I could just use a double clip angle with an endplate using post-installed expansion or adhesive anchors. Then, field x-ray surveying revealed that the existing main reinforcement of the square concrete columns had a concrete cover of +/- 4" to 6", rendering the usual mechanical/adhesive anchors inadequate for the heavy loads (90+ kips) at these connections.
So I'm considering thru-bolting through the entire column. What failure modes would you consider for through bolting the endplate through the column with some fishplates on the other side? So far, I can think of ductile steel shear failure and concrete bearing at the anchors. I'm not sure if side blowout is a possibility or whether I can consider the #10/#11 main rebar + column ties as confining it all. Pryout is not possible because it is a thru-bolt but I can't help but think there could be additional failure modes to consider. Maybe steel failure preceded by concrete edge spalling?
Ex. - W36 beam with endplate to 26"x26" reinforced concrete column.
At first, I decided that I could just use a double clip angle with an endplate using post-installed expansion or adhesive anchors. Then, field x-ray surveying revealed that the existing main reinforcement of the square concrete columns had a concrete cover of +/- 4" to 6", rendering the usual mechanical/adhesive anchors inadequate for the heavy loads (90+ kips) at these connections.
So I'm considering thru-bolting through the entire column. What failure modes would you consider for through bolting the endplate through the column with some fishplates on the other side? So far, I can think of ductile steel shear failure and concrete bearing at the anchors. I'm not sure if side blowout is a possibility or whether I can consider the #10/#11 main rebar + column ties as confining it all. Pryout is not possible because it is a thru-bolt but I can't help but think there could be additional failure modes to consider. Maybe steel failure preceded by concrete edge spalling?