NicolasK
Electrical
- Dec 12, 2003
- 8
I want to connect the secondary side of two 120/240V transformers in series to get 480V. The transformers are 10 kVA units (additive polarity). The H1 bushings will be tied to the same primary phase, each with its own fused protection (cutout). H2 bushings will be tied to the system neutral. On the secondary side, tie X3 of transformer A to X1 of transformer B. Then I should have 480 V across the remaining X3/X1. For the service wire ground, can I tie it directly back to the system neutral(ground)?
Assuming I use identical transformers(voltage rating, imp., etc.), will this work? Anything I need to watch out for?
Thanks.
Assuming I use identical transformers(voltage rating, imp., etc.), will this work? Anything I need to watch out for?
Thanks.