flapdash
Electrical
- Nov 6, 2009
- 3
I am connecting three switched power supplies in series. Each supply is 30VDC, to give 90VDC output. The current rating on each 30VDC module is 50A. I've verified that series operation is supported by the manufacturer (Astec/Emerson). The load is a motor, and I plan to install shunt regulation and capacitance near the motor to help with this inductive load and guard against harmful regeneration.
Someone recommended putting diodes between each module, as shown in the picture attached to this post (D1, D2, D3...see picture). Why? Something about one module's positive terminal going lower than the adjacent module's negative terminal and therefore these diodes would guard against unwanted current flow in the "wrong" direction?
Can anybody provide an explanation of why D1, D2, and D3 might be necessary?
Thank you!
Someone recommended putting diodes between each module, as shown in the picture attached to this post (D1, D2, D3...see picture). Why? Something about one module's positive terminal going lower than the adjacent module's negative terminal and therefore these diodes would guard against unwanted current flow in the "wrong" direction?