Michael2009
Petroleum
- Jun 24, 2010
- 49
Hi Guys,
I am confuse while checking my contractor drawing.
Motor FLA = 47A
MCB 3P = 80A (Installed outdoor at 55degC inside enclosure, derating to 72A)
Power rating = 480V 3 phase 60Hz
Cable Run around 50 meter
Cable selected 35 mm2 (Current capacity in catalog 136 A)
While I doing the checking
Cable derating current is around 87A
With consider the rule of thumb
FLA (A) < MCB (A) < CABLE (A)
47A < 72A < 87A
All looking fine.. but if I look at motor load only 47A .. correct selection shall be 47A x 1.25 = 58.75A next jump is 63A MCB.
It is ok to use 80A breaker? Look like oversize. But the rule of thumb is fulfill... I am confuse ...