I have 10 machines, each with a specified maximum machine load of 168kVA. Each has 126 1kW motors, 2 5kW motors and some Inverters, controls, electronics, etc.
The machines run at 380VAC. They are powered by a 600V bus through a 1000KVA 600:400 stepdown Transformer.
I have an old record of an electrician's current reading on one machine drawing 60 Amps on the primary of a smaller 600:400 step down Trans when powered separately.
60x600x1.73=62kW
10 machines on the 1kVA transformer represent a loading of
10x62kW= 620kW or 62% loading on the transformer. That makes sense.
But why does the manufacturer specify a 'max machine load' of 168kVA? That would mean that my 1000kVA transformer is 168% loaded!! Can anyone explain this?
I am installing additional machines from this company and they are specifying a max machine load of 207kVA for the new machine. It has 152 1kW motors and approx. 10kW of additional motors and inverters, controls, etc. similar to the old machines. I need to size a new transformer and bus bar, cable, etc. for the new equipment...
60x600x1.73=62kW