I don't think it is such a standard. NEC ch.9 recommends the filling factors [it is not compulsory]. There are some other recommendations from other experience as this for instance:
"UK wiring regulations BS7671, recommend that the total cross sectional area of the sum of the individual cables should not exceed 40% of the cross sectional area of the conduit"
And other stated:
"BS7671-2008 provide tables for cable and conduit factors, these can be found in the current IEE On Site guide BS7671-2008 Appendix 5 Pages 117 to 120"