I used IEC 61936-1, Table 1, "Minimum Clearances in Air" for given BIL levels in reviewing some equipment. Can't find my copy, but one of my notes quoted the table, "95 kV BIL, 160 mm"
Manufacturer's can use smaller distances if they test the equipment to prove no flash over.