Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Conductor sizing for multiple VFD's

Status
Not open for further replies.

viking684

Electrical
Joined
Dec 2, 2013
Messages
13
Location
AS
I was wondering if someone could please tell me how to calculate conductor sizes for 2, 3-phase, 30- Hp, 460V VFD's, controlling 2, 30-Hp, 3 phase, motors? Would it be done the same way you calculate multiple motors (125% FLC of the largest motor and add the other FLC's)?
 
You are a little sparse on details here.

Where are you located? This is an international forum, although we can deduce to about 90% that you are in North America by virtue of your use of 460V and HP rather than kW but the U.S. And Canada have slightly different codes when it comes to conductor sizing. Also which conductors are you referring to, from the VFD to the motor, or from one feeder to both of the VFDs or separate feeders, one to each VFD?


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top