Typically conductors experience only primary creep and thus obey the power law of, strain = C*time^m for a constant stress & temperature level. Here C, m are creep coefficients. In general, C depends on both temperature and the stress level with a similar equation C=K*T^n*(stress/uts)^k, where K,n,k are also coefficients, T is the temperature in absolute degrees, and uts is the ultimate tensile strenght of the cable. Typically m=0.16, although it varies between m=0.13..0.19. The other coefficients I don't remember.
In real life the tension & temperature changes through out time. Typically creep is considered at the everyday temperature but with steps of stress levels as mentioned at above posting. In addition, there might be Elevated Temperature Creep, where the cable is operated for a few hours at high temperatures for additional creep but this only applies to cables with a high content of aluminum where the stretched aluminum may reach a compressive state.
John Alexiou
Alcoa - SAG10/Vibrec Development.