I am looking for some feedback on a situation and not sure I am being fed a load of BS.
The problem is a recently completed ~3,000 SF 1-story office building experiencing high indoor RH (70%+) levels.
Building is in Charleston, SC, USA.
HVAC consists of 2 DX split heat pumps, OA is ducted direct to an OA louver into RA duct of each HP, motorized damper connected to DDC, interlocked with HP compressor.
HP indoor units are in an indoor mechanical room. Walls between mechanical room and occupied space is CMU up to about 10', then gyp-board on metal studs to roof. These walls are "sealed" to create an air barrier. AHUs are off-the-shelf draw-thru units, =< 5 tons, installed vertically air flow moving up thru unit.
Ventilation for mechanical rooms is via an exhaust fan. Make-up for this fan is a louver with motorized damper interlocked with fan. Make-up air for mechanical room is not filtered or conditioned. This fan is controlled via thermostat and when on.
Condensate trap for the indoor units are ~6" deep, with 1/2" drop between trap inlet and trap outlet. (This is per a detail on the design documents.)
We recently did a walk through of the building with the designer of record and a rep for the installed heat pump and discussed the findings afterwards. Aside from making improvements to the controls strategy, there was one other item that I am not sure about, the construction of the condensate traps. The manufacturer rep made the claim that with the trap inlet/outlet being so close in elevation, that when the unit is blowing air, the condensate in the trap is being sucked back into the unit and the trap is unable to allow condensate to drain properly. As a result, the condensate is being pulled out of the drain pan and back into the air stream.
Thoughts? Experience?
Thanks in advance.
Thanks in advance.