The diameter of the drain line pipe should be at least the same diameter as the connection provided on the evaporator’s drain pan.
The pitch of these drain lines is also an important part of the overall installation. It is generally recommended that the horizontal section of pipe have a pitch of at least 4 inches per linear foot. This will be adequate to drain the water away from the evaporator and prevent it from draining too slowly or standing in the line.
Drain lines should be run to an open drain and never be connected directly to a sewer system. This will prevent sewage from backing up into the evaporator in the event the sewage system backs up.