ChasBean, I think he is talking about ambient temps being over 66 degrees, meaning that warmer outside air has higher capacity to hold grains of moisture, as he mentioned humidity as well.
Another option to decrease cfm and therefore velocity over the coil is to reduce supply air temp. He may want to try to change the supply air discharge setpoitn to 52 degrees or so. Also, 6 years is a long time for a balance, especially in this industrial setting. Get a TAB report done asap.
The other issue could be with the condensate drain p-trap not being deep enough for the negative static pressure of the fan. If the difference in trap height is less than the inches of static after the coil, then it is not deep enough and condensate will get sucked out, causing leakage.