Careful with a statement like "The density of the concrete itself may be less for heavily reinforced structures because of the difficulty in placing and vibration that is caused by more steel than normal." Since it only applies in poorly-constructed projects and indicates that the structure will not have the design strength. If you allow this, it's your license on the line.
Hydration of concrete requires somewhere around 0.25 w/c ratio (although this is debated, it is the theoretical requirement.) As noted, the trapped moisture in voids also sequesters a fair amount of moisture. Do not count on evaporation of any of the moisture in the concrete, since properly cured concrete retains most of the mix water. Also, aggregates are processed into ready mix at a saturated, surface dry (SSD) condition, so the water added to the mix is not all that is there or all that remains for a long period after placement.