Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Concrete Tank Slab

Status
Not open for further replies.

Kowycz

Civil/Environmental
Joined
Dec 30, 2009
Messages
14
Location
US
I am currently revising a concrete clarifier slab thickness and reinforcement. The clarifier is being relocated on the site from a poor soil condition location to a relatively good soil condition location. We are in the process of getting new bore holes drilled in the exact location; however a couple bore holes were almost in this location from the original borings.

Tank dimensions:
Diam = 60'-0"
SWD = 12'-0"

My supervisor instructed me that he would just make the slab 2'0" thick and there really isn't any design involved save the bearing capacity of the soil and flotation calculations.

I was just interested in getting a second perspective on the situation.

Thanks
 
You mention flotation. If flotation governs (compared to bearing), perhaps the dead weight of a 2' thick slab is needed to overcome flotation (even if 2' thick is more than enough for bearing). The correct answer depends on the details.

According to the flotation calculations 18" is the depth necessary. I was just wanting to ensure there wasn't something else I might be overlooking.
 
We make clarifier slabs as thin as 8 inches away from the thickened edges. Except at the walls, they pretty much just pass the liquid load right to subgrade. So 18 inches should be plenty thick.
We also like to put a 2 inch grout topping, placed by the clarifier mechanism. This provides a better tolerance for the sweeps. Other designers don't do this, so it's up to you. And I wouldn't count on this for flotation resistance.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top